Hello all
Lets call
- Pd The design pressure (internal pressure)
- St The allowable stress of the prevalent piping material at Test temperature
- Sd The allowable stress of the prevalent piping material at Design temperature
(x = multiplication)
Hydrostatic test for piping system Pt=1.5xPdx(St /Sd)
or 1.5 times the design pressure multiplied by the stress ratio at test temperature to design temperature
As you write wrote that the set pressure for the PSV is 100 psi so the design pressure must be less than 100 psi, so the 1.5x285 either contain the stress ratio (correction for temperature) or the design temperature greater than the test temperature.
If you give us the prevalent construction material , design temperature , test temperature and design pressure, I will calculates for you the hydrostatic pressure (as given by B31.3)
For the ¨PSV It must be blocked or removed during the hydrostatic test
Regards
------------------------------
Elhazel Aymen
Mechanical engineer
Groupe Chimique Tunisien
Tunisia
------------------------------
Original Message:
Sent: 03-27-2024 09:33 AM
From: Jesse Kelton
Subject: Hydro Test Pressure
I have a section of piping that I am replacing with a 150# flange. This piping system has a PSV with a set pressure of 100psi. Is hydro testing the newly fabricated piping to 1.5 x 285psi the only option? Or is hydro testing to 1.5 x 100psi allowed? Thank you.
------------------------------